I’m in the middle of replacing a cracked electric hob with an induction hob.
I’ve removed the old hob- it appears to have the twin and earth supply cable hard wired into the hob. There is no junction box visible.
The replacement hob comes with an attached cable. On removing the covering plate on the hob where the cable inserts it doesn’t appear that it is designed to have the supply cable directly wired into it. The terminals are not visible.
I’m going to connect the fixed cable on the new hob to the supply cable, but was wondering if I’ll be ok to use Wago connectors for the job (covered with insulating tape)?
The maximum power of the new hob is ‘6.400 W’ (I’m assuming that’s 6400W rather than 6.4W!) so at 230V I was calculating just under 28 Amps.
I’ve got both Wago 221 and 222 connectors. Would they be suitable?
If not, what would be best? I’m hoping I’ve got the bits I need, otherwise I need to refit the cracked old hob to cook dinner tonight!
I’ve removed the old hob- it appears to have the twin and earth supply cable hard wired into the hob. There is no junction box visible.
The replacement hob comes with an attached cable. On removing the covering plate on the hob where the cable inserts it doesn’t appear that it is designed to have the supply cable directly wired into it. The terminals are not visible.
I’m going to connect the fixed cable on the new hob to the supply cable, but was wondering if I’ll be ok to use Wago connectors for the job (covered with insulating tape)?
The maximum power of the new hob is ‘6.400 W’ (I’m assuming that’s 6400W rather than 6.4W!) so at 230V I was calculating just under 28 Amps.
I’ve got both Wago 221 and 222 connectors. Would they be suitable?
If not, what would be best? I’m hoping I’ve got the bits I need, otherwise I need to refit the cracked old hob to cook dinner tonight!