Wiring in a BDR91 to Combi Boiler

Joined
19 Jan 2019
Messages
2
Reaction score
0
Country
United Kingdom
Hi All,

Just got my Evohome kit through the door the other day and was looking to get it up and running this weekend. My existing relay is also honeywell (R6660D / HC60NG) so should be a fairly straight forward swap out but whilst looking at the existing wiring I noticed a couple of quirks / potential issues and just thought it would be wise to get some opinions before getting stuck in.

Here is the existing setup:

Current setup.jpg


So 2 things....

1. For some reason the Live and Neutral seem to be when going into the relay, why would this be? Should I preserve this when wiring in the BDR91 or put it back to normal?

2. There isn't a place for the earth cable on the BDR91, should i leave it disconnected (both ends) and remove it?

Ending up with this....

BDR91.jpg


or obviously with the live and neutral in their normal positions....

What you reckon?

Thanks
Brew
 

Attachments

  • BDR.jpg
    BDR.jpg
    145.5 KB · Views: 532
  • Boiler.jpg
    Boiler.jpg
    153.1 KB · Views: 394
  • HC60NG.jpg
    HC60NG.jpg
    159.5 KB · Views: 540
For some reason the Live and Neutral seem to be when going into the relay, why would this be?
It was installed by a moron and his blind assistant.

2. There isn't a place for the earth cable on the BDR91, should i leave it disconnected (both ends) and remove it?
Leave connected at the boiler, do not connect to the new BDR91.
 
It was installed by a moron and his blind assistant.


Leave connected at the boiler, do not connect to the new BDR91.

Yeah thought as much, though it has worked without issue since moving in....

So I'll wire the live and neutral as normal and disconnect the earth wire between the boiler and bdr91?

Nice one (y)
 