Radiators are totally working fine.. equal heat bloom on the Thermal imaging camera, but it shows the hot water is only getting halfway from the pump.to the cylinder, even when 3W valve is both positions
All 3 Radiators are all hot which proves flow from pump to 3W valve port A to rads and return.
So my initial thoughts are..
blocked 22mm flow pipe from valve port B to cylinder.
Or blocked cylinder.
Or blocked 22mm from cylinder to common return.
Or a combination of all 3!
Wierdly the HW cylinder is piped with flow from boiler at the bottom of the coil and the return at the top of the coil.
System is fitted with magnaclean filter and that has minimal magnatite, system is filled with x100 and has been regularly serviced.