Hi,
I have moved into a new build and have a problem that the builder keeps saying is normal, please advise.
The system is a Vokera Mynute boiler with pressurised hot water tank and 2 heating zones. The heating works fine downstairs and upstairs but when it's supposed to be off upstairs and on downstairs the radiators upstairs are still getting hot. I suspect the motorised valve for the upstairs zone isn't closing properly. Isn't the whole point of having 2 zones so that they can be controlled independently? The builder has tested it several times and thinks this is fine. Initially they said it's because the upstairs zone was set to 15 °C between heating periods and the temperature must have been below that, but I've done a test where I set the upstairs zone to off and still had the same problem.
Thanks!
I have moved into a new build and have a problem that the builder keeps saying is normal, please advise.
The system is a Vokera Mynute boiler with pressurised hot water tank and 2 heating zones. The heating works fine downstairs and upstairs but when it's supposed to be off upstairs and on downstairs the radiators upstairs are still getting hot. I suspect the motorised valve for the upstairs zone isn't closing properly. Isn't the whole point of having 2 zones so that they can be controlled independently? The builder has tested it several times and thinks this is fine. Initially they said it's because the upstairs zone was set to 15 °C between heating periods and the temperature must have been below that, but I've done a test where I set the upstairs zone to off and still had the same problem.