I'd be looking for a boiler engineer that understand and is happy to work on your system. It may be a simple fix, but I suspect a 1995 boiler is unlikely to have a permanent pilot light. From your description I would say it is overheating, and causing the overheat protection to kick in. Overheating is usually down to poor circulation, (and kettling indicates the same problem), so the problem lies within the system rather than the boiler. I would be reluctant to change the boiler unless it was completely knackered, a new boiler will take a long time to pay for itself in gas savings, if at all during its lifetime.
Sludge and corrosion are possible issues, as is a weak pump. Pump head has been changed at some point, can you get to it and see what speed its set to? The Magnaclean would also be worth checking, if it contains a lot of crud it, (apart from needing cleaning out!), would indicate a dirty system. (Check pump speed first though.)
Sludge and corrosion are possible issues, as is a weak pump. Pump head has been changed at some point, can you get to it and see what speed its set to? The Magnaclean would also be worth checking, if it contains a lot of crud it, (apart from needing cleaning out!), would indicate a dirty system. (Check pump speed first though.)