Hi,
A strange fault has developed over the last week or so in our Worcester Bosch 40CDi (conventional) based central heating/hot water system.
Several times over the last week or so there has been load banging coming from the boiler when it first fires up in the morning. I was able to see what was happening yesterday and the boiler temperature was hitting the high 90s and which point steam was obviously being produced causing the banging. At which point the boiler went into some sort of recovery mode and after a couple of minutes fired up again and everything then works normally for the rest of the day. The hot water produced by the boiler is of the correct temperature, I have checked all the radiators (which heat up normally) and there is no air in the system that I can detect and the header tanks are full.
We had the central heating pump changed about 5 years ago, and about two years ago I changed one of the motors on the 2 motorised valves we had in the system.
There is obviously a problem with water getting to the boiler which corrects itself on the second attempt at firing up. This makes my think that something is sticking or getting jammed which is then starting to work on the second attempt.
Is there anything in the boiler which could be causing this (i.e. do I need to get Worcester Bosch out to fix it) or is it more likely to be a pump or valve sticking in the airing cupboard?
Any thoughts on what it might be or fault finding techniques I could try?
A strange fault has developed over the last week or so in our Worcester Bosch 40CDi (conventional) based central heating/hot water system.
Several times over the last week or so there has been load banging coming from the boiler when it first fires up in the morning. I was able to see what was happening yesterday and the boiler temperature was hitting the high 90s and which point steam was obviously being produced causing the banging. At which point the boiler went into some sort of recovery mode and after a couple of minutes fired up again and everything then works normally for the rest of the day. The hot water produced by the boiler is of the correct temperature, I have checked all the radiators (which heat up normally) and there is no air in the system that I can detect and the header tanks are full.
We had the central heating pump changed about 5 years ago, and about two years ago I changed one of the motors on the 2 motorised valves we had in the system.
There is obviously a problem with water getting to the boiler which corrects itself on the second attempt at firing up. This makes my think that something is sticking or getting jammed which is then starting to work on the second attempt.
Is there anything in the boiler which could be causing this (i.e. do I need to get Worcester Bosch out to fix it) or is it more likely to be a pump or valve sticking in the airing cupboard?
Any thoughts on what it might be or fault finding techniques I could try?