I'm worried about fitting a gate valve because I want the hot water cylinder to get a good amount of heat when it needs it. The zone valve is working because it switches on and off with the programmer. I think the cylinder thermostat needs replacing because it's doing nothing to cut off the zone valve (no sound of a 'click' when I turn the dial down).
I'm intrigued by this low loss header concept. You're the third person to suggest hydraulic separation on this thread; so I will definitely have to look further into this. How does your set up look?
If you boiler does not deliver water at a temperature high enough to heat water in the cylinder to its thermostat setting, that thermostat will never be satisfied. Why not time the water heating to night time with a boost when heating not required.
What setting are you running the boiler at when heating water
Some boilers, do not think yours has that facility, can be set to run at different temperature, so for hot water heating boiler would run at higher temperature
Homeserve fella talking rubbish. You have a 37kw boiler. How is a 38kw boiler going to help the situation. Looking at the system stripped down, the heat exchangers for your boiler or 438 will be almost identical. System boiler has internal pump, 438 no pump so external required.
Some excellent advice already posted.
Perhaps it could be suggested you get couple of clamp thermometers and plot out temperature chart at each radiator, cylinder and at the boiler of flow and return to access where the water is going or not
Attended an 'erratic hot water delivery' call yesterday.
Used two Testo clamp thermometers to show customer boiler working fine as indicated in manual. Issue- incoming water at 4 degree C and boiler raising the temperature by 35 to deliver 40 degrees of not do hot water to the tap. Water delivery stable. Have used these Bluetooth devices to figure what is actually happening. Has been a good investment.
Look at Honeywell Evohome to heat rooms as they are occupied rather than the whole house