The full section on socket outlets is as follows:
7.2.2 Socket-outlet circuits
The length represents the total ring cable loop length and does not include any spurs.
As a rule of thumb for rings, unfused spur lengths should not exceed 1/8 the cable length from the spur to the furthest point of the ring.
The total number of fused spurs is unlimited but the number of non-fused spurs is not to exceed the total number of socket-outlets and items of stationary equipment connected directly in the circuit.
A non-fused spur feeds only one twin socket-outlet or one permanently connected item of electrical equipment. Such a spur is connected to a circuit at the terminals of socket-outlets or at junction boxes or at the origin of the circuit in the distribution board.
A fused spur is connected to the circuit through a fused connection unit, the rating of the fuse in the unit not exceeding that of the cable forming the spur and, in any event, not exceeding 13A. The number of socket-outlets which may be supplied by a fused spur is unlimited.
The circuit is assumed to have a load of 20A at the furthest point and the balance to the rating of the protective device evenly distributed. (For a 32A device this equates to a load of 26A at the furthest point.)
I think this whole piece is very clumsily written. The first sentence being stuck at the top when it would make more sense to put it after the second sentence. "rule of thumb" is wishy-washy and old fashioned. Either it is or it isn't. If it is a rule, then take the ROT bit out.