The RCD like the MCB comes in different flavours, the two sizes normally refereed to at 300 mA used to protect from fire, and the 30 mA used to protect from shock, but the 100 mA was very common to allow the use of a TT supply in relative safety, back in the days before RCD's were required for personal protection.
The equipment used in the house has changed over the years, I look at my own house, inverter fridge/freezer, freezer, washing machine, and induction hob, plus of course loads of other switch mode supplies, and I have realised my type AC RCD
is not good enough, and I had had to order type A RCD
to replace it, both are 30 mA at 40 mS but because I am using items like the induction hob it's possible they will not trip when they should.
However I had a read of the Electrical Safety Council best practice guide 4 issue 5 and there is nothing about checking type of RCD used, it seems we now know the danger, but as yet have not caught up, so not included in an EICR (Electrical Installation Condition Report) which has also been the subject of debate of late as now a legal requirement with some rented property, so it was up to the electrician to consider what required testing and inspecting who was guided by his course and exam C&G 2391 but now it seems he needs to follow some laid down criteria which to date I have been unable to find.
[SIZE=4][B]SSE Electrical Wiring Cover [/B]advert[/SIZE] said:
Electrical Wiring Inspection
An initial inspection is a visual inspection of your home electrical wiring and fuse box and an earth loop impedance test, and may be deemed necessary if your house is over 15 years old, hasn’t been rewired in the last 15 years or has an old style fuse box. "Fixed electrical wiring system" covers electrical wiring, fuse box, light fittings and switches, wall sockets and shower isolation switches.
That does not sound like a full EICR, it sounds more like the type of checks the suppliers use to do before connecting you up.
[SIZE=4][B]SSE Electrical Wiring Cover [/B]advert[/SIZE] said:
[SIZE=4][B]SSE Electrical Wiring Cover [/B]advert[/SIZE] said:
- Repairing the power supply to your property or the electricity meter
- Any items that do not form part of the fixed electrical wiring system
- Electrical heating equipment
- Major rewiring works. This Agreement only covers repairing Fault
So I would think a shower comes under heating equipment, and £63.60 is less than most charge for an EICR without any insurance so as to what is inspected and tested is unlikely to equal a proper EICR, if it did then landlords would be signing up for that by the droves.
The BS 7671 is considered as the standard most work by, and with a few exceptions each time a new version is released it states it is for new work done after the date it comes into force, so a house built in 1960 could still be used today as long as owner occupied, there is no need to update, however any updates must comply with the latest edition, so we get the situation where to fit some thing which seems rather minor, becomes major because the system needs updating before it is fitted.
We see phrases such as like for like, but in real terms that rarely exists, some thing has changed, if only the manufacturers instructions. And clearly in 1960 no one had an induction hob fitted. So in real terms your old fuse box has reached its use by date, the changing of the fuses to MCB's did extend its life, but if you want to use modern appliances then the box needs to be upgraded.
If the supply is TN then there is not really that much danger using a type AC RCD with this
logo, the RCD is a secondary protection, and likely I am going OTT in changing mine, however if the supply is TT (means it uses an earth rod) then the type of RCD fitted is far more important, you want to see
logo (Type A) or better like this
(type F) or this
(type B) although as far as I am aware the latter two only seem to be used with domestic with electric car chargers and solar panels.
As to size of cable the idea of using a micrometer and calculating the cross sectional area seems too complex, I have some red, blue, and yellow crimps, plus uninsulated 10 mm and 16 mm, and I simply try a crimp on the cable, is the yellow 6 mm crimp will not fit assuming the wire not crushed, then likely it is 10 mm or 16 mm, however it is unlikely to be anything better than 6 mm² it was so much easier before we went metric, I was taught in the age of 7/0.044 cable I could easy measure 0.044 inches with micrometer and can count to 7.
In real terms we don't use a shower for long, so a 7.5 kW shower may be just on the limit of 32 amp, and an 8.5 kW is 37 amp, but we tend to have finished showing long before the MCB or cable reaches a temperature where likely to type or get hot, 9.5 kW at 41 amp is stretching it is little too much, but unless colouring their hair, even then it tends to work most of the time without too much of a problem, however the continual over heating of the MCB tends to make them go weak, and the time you can shower for slowly reduces, but with a 32A MCB it does its job and protects the 6 mm² cable tripping before the cable gets too hot, the only real problem is when the cable warms and cools it can compress in the terminals and over time become loose, and once it get loose it gets a bad connection and heats up to a very high heat, causing fire. We had a service schedule to stop this, torquing up the screws, however it did not really work, as this also compressed the cable and had some cables break at the terminals, but at least no fire. I have never seen anyone do a service on a house. There are units that are claimed to disconnect the supply it is detects sparking, but personally having the RCD trip is bad enough, fitting a surge protection device (SPD) OK when it goes it just shows red in the little indicator window, but there has to be a limit.
Anyway interested in the SSE testing, how long does it take them, that's a good indication on how much tested.