ok thanks EFLImpudence do you think its looking more like the 13amp fused spur has been run at long periods and killed it? Assume you agree with having a dedicated 16A Breaker and 20A DP ?
If your theory is correct and the floor is faulty, it should trip the 16A Breaker correct?
If so (and if its not... that requires addressing asap) then I struggle to envisage how it could fail in the manner discribed by eveares without tripping the RCD
It could have just been a loose connection which caused the overheating.
I doubt the UFH can cause an overload.
Then there is no way the resistance could reduce and hence the current rise.
thanks Mike, do you agree then for this to be installed on a 16A Breaker with 20A DP instead?
(Even though 2.5mm on 32A is not designed correctly as the cable is drawing only 10A and the load protected by a 13 FCU, I would not expect this be a danger, in my opinion not right but dangerous no)
Not by intelligent people.
The 2.5mm that was shared with the 32amp (for kitchen hob) has been moved onto its own 16AMP breaker as you have all advised. I have ordered a 20A DP switch to replace the 13A Fused spur as suggested.
I noticed the fuse is slightly warm to touch (but not red hot) I read a post from another user on this Fourm discussing that its 'normal' for them to get warm due to the amount of constant load (i.e. heating the floor). As this is drawing 10AMP I assume warm is ok ?
A full short will be covered by the 32A MCB - after all, no different than a socket spur.But how about a partial or full short before the 13A Fuse, however unlikely. Certainly is not compliant with BS7671.(Even though 2.5mm on 32A is not designed correctly as the cable is drawing only 10A and the load protected by a 13 FCU, I would not expect this be a danger, in my opinion not right but dangerous no)
I'm not sure you can have a partial short.
Exactly. I do wonder how people think this is different to a single length of 2.5mm spurred from a ring final on a 32A breaker.
A flux capacitorI meant a high impedance short, Or is that a contradiction in its self. Does a short have to be in the range of a few Ω's or less; What would an unintended load due to a fult between line and neutral be called then???