The welder is a 180 ac/dc inverter.
It's spec is as follows.
Single phase 230v
Input frequency 50/60Hz
Fuse rating 16 A Slow Blow
Open circuit voltage 50 - 60 V
Max primary current 29.5 A
Max power consumption 6.8 kVA
Main supply protection 25 A
Power factor (Cos) 0.98
The circuit I want to install for the welder will be in a new garage fed from a new CCU with a 63A RCD which is fed from another CCU with 16mm XLPE SWA (3core) I'm not sure what to protect this feed with on the other CCU, it's a split board with 80A RCD's....Anyway I digress.
In the garage I will have a washing machine, tumble dryer and a small chest freezer. The washing machine and tumble dryer will be on at the same time so a 25A load will happen sometimes.
I'm assuming 0.5A for a 100L chest freezer.
I plan to use a 2.5mm t&e ring (32A MCB) with single switches spurred to 1gang unswitched 13A outlets for the washing machine, tumble dryer and chest freezer then another 2.5mm t&e ring (32A MCB) with 4x2gang 13A outlets for strimmers, general portable devices etc.
Also a 1.5mm lighting circuit (6A MCB)
Should I run a 6mm t&e radial to a switched 32A commando socket with a 32A MCB Type C?
The reason I'm contemplating this is because the welder has a max power consumption of nearly 28A and its max primary current (I assume when starting up or striking an arc) is 29.5A
It would be a bonus if someone can explain how the welders electrical design works. I mean 29.5A with 25A protection and 16A Slow Blow fuse confuses me and I don't know exactly how the duty cycle effects these figures (50% @ 180A & 100% @ 140A)
TIA
It's spec is as follows.
Single phase 230v
Input frequency 50/60Hz
Fuse rating 16 A Slow Blow
Open circuit voltage 50 - 60 V
Max primary current 29.5 A
Max power consumption 6.8 kVA
Main supply protection 25 A
Power factor (Cos) 0.98
The circuit I want to install for the welder will be in a new garage fed from a new CCU with a 63A RCD which is fed from another CCU with 16mm XLPE SWA (3core) I'm not sure what to protect this feed with on the other CCU, it's a split board with 80A RCD's....Anyway I digress.
In the garage I will have a washing machine, tumble dryer and a small chest freezer. The washing machine and tumble dryer will be on at the same time so a 25A load will happen sometimes.
I'm assuming 0.5A for a 100L chest freezer.
I plan to use a 2.5mm t&e ring (32A MCB) with single switches spurred to 1gang unswitched 13A outlets for the washing machine, tumble dryer and chest freezer then another 2.5mm t&e ring (32A MCB) with 4x2gang 13A outlets for strimmers, general portable devices etc.
Also a 1.5mm lighting circuit (6A MCB)
Should I run a 6mm t&e radial to a switched 32A commando socket with a 32A MCB Type C?
The reason I'm contemplating this is because the welder has a max power consumption of nearly 28A and its max primary current (I assume when starting up or striking an arc) is 29.5A
It would be a bonus if someone can explain how the welders electrical design works. I mean 29.5A with 25A protection and 16A Slow Blow fuse confuses me and I don't know exactly how the duty cycle effects these figures (50% @ 180A & 100% @ 140A)
TIA