Maybe I should put a 45A RCD in the garage CCU and protect it with a 50A MCB in the other CCU that feeds it. .
NO. As I said two RCDs in line is pointless. RCDs do not trip on over current, they protect against imbalance typically caused by leakage to earth. The current rating is the safe load not a trip.
The current rating is the safe load not a trip.
I think you're quibbling a bit - since, if running an RCD at its rated 'maximum current' was 'not safe', I think something about the stated ratings would be seriously wrong!And if you mean Main switch type Rcds, surely the rating in the OPs boards which he says, one has 63A and the other 80A Are the MAXIMUM load, NOT the safe load.
Rubbish, the current rating on the device 45A is the trip rating, it is obvious he means an RCBO which is a form of RCD
Maybe I never explained it very well but it is not that hard to see what I need.And if you mean Main switch type Rcds, surely the rating in the OPs boards which he says, one has 63A and the other 80A Are the MAXIMUM load, NOT the safe load.
No wonder we need flame retardent boards now!
Obvious to whom? No one else on here has assumed he means RCBO. Anyway you must never assume with electrics if you want to live to enjoy retirement!
I don't have the CCU, the whole question is hypothetical, the only thing that can't be changed is the 16mm SWA.No one assumed, as I say it was obvious
1, For one he has a CU board with a 63A Rcd main switch, how on earth could he fit anything other than an RCBO without butchering the board.
2, Apart from an Rcbo what other RCD exists in a 45 amp rating
The CCU is already protected by a 80A DP switch fuse by the way, should I put another one in to protect the garage CCU?You'd be best using a BS88 or BS1361 cartridge fuse to supply the sub mains given the proposed loads, and then arrange RCD protection in the garage CU as and where required.
Ok I'm not saying your not right, don't be so touchy, I'm just giving more information about what the situation is incase it makes a difference to the design in regards to safety. While I'm at it I might as well explain that the new CCU will be in an extension which is Henley blocked and has the 80A switch fuse I mentioned. It will be interesting to see if the electrician chooses to use another switch fuse or rely on the MCB in the RCBO.You can do what ever you want. It's not going to affect me. Using a cartridge fuse rather than a circuit breaker to protect the submain will guarantee discrimination and give you a much more reliable installation, but if you want to use a circuit breaker that's entirely up to you.
How it's wired is up to your electrician to decide, but normally a switch fuse henleyed of the incommer is the best way to achieve this.