Thanks, theoretically boilers are sized based on HL and design temp, since rads are almost, always oversized.
I didn't know about HL of my propety and previous 24kw boiler worked with 8min on and 12mins off cycle (in slightly less cold weather the off time was doubled than on time), I was told that boiler is way oversized for my heat loss.
I did HL and came up with half of what boiler could output! (11 kw in my case).
As you say, flow temperature can be increased to get the required heat output (though may be not as efficiently or in condensing mode).