Now, how to connect it in to mains supply?
Sorry but the best way for a safe installation is to employ an electrican.
Now, how to connect it in to mains supply?
So is the way that some cables are too close to the floor.That junction box though, is a bit rough.
A functional Earth is not a protective conductor. It's all irrelevant though, as we were not discussing functional Earthing.543.7
If the intention were that CPCs should be considered as "Live conductors",
As I said, if 'energizing' means deliberately connecting a conductor to such a potential, then that's what the BS7671 definition seems to be saying.A Live conductor is one that has a potential different to the ambient ( Ground or equipotential "Earth" ) potential. it does not have to be carrying a current to be Live.
Quite - if the above is true, then so probably is this. However, as I said, it makes little sense in terms of some regulations - do you really think that it is 'intended', sensible or necessarily 'safe' to include isolation of the CPC in the name of 'isolation' (in TT systems)?If the Neutral is to considered as Live conductor then any conductor connected to the Neutral will have the same potential as the Neutral. Hence if the Neutral is to be considered as a Live conductor then the MET, CPC and all items bonded to the MET have to be considered as being Live as well.
That is really going to depend on the definition of "energise"."Energized" is not defined, but would you really say that we "intentionally energize" CPCs? For what it's worth, I wouldn't.
I'm sure it is.I would therefore suggest that, attempts on the part of anyone to 'be clever', aside, the generally-accepted view that CPCs are not 'live conductors' is both sensible and almost certainly the intention of BS7671.