All very true.All three of these options to add a number of additional sockets between 2 existing on the ring final using junction boxes comform to the regs ...
Many people would probably share your preference although, in reality, I don't think it really makes appreciable difference - there's not even much difference in terms of 'the number of conductors inserted into terminals'.My preference would be .... without junction boxes.
The only actual benefit is one less in-line join over the middle option and not having to find a place for it.All very true.
Many people would probably share your preference although, in reality, I don't think it really makes appreciable difference - there's not even much difference in terms of 'the number of conductors inserted into terminals'.
Kind Regards, John
I don't think that differs all that much from my "no appreciable difference" viewThe only actual benefit is one less in-line join over the middle option and not having to find a place for it.
No it doesn't apart from being a tiny bit tidier.I don't think that differs all that much from my "no appreciable difference" view
Kind Regards, John
A final circuit is one that supplies socket outlets or current using equipment directly, a distribution circuit is one that runs from one distribution board to another.Thanks for the replies. Terry yes that's my question. What do you mean by 'final' circuit though?
Neither part P, nor the associated notification requirements get into such minutae.I wasn't going to extend the ring as my understanding is that's not allowed without the part P domestic installer qualification.
Terminating conductors in this context refers to connecting them to terminals.Aptsys, by 'terminating conductors', do you mean ensuring they reach a socket?
I would imagine that most people would agree with that, particularly for the terminals in "13A" BS1363 sockets, but ...Exactly how many wires is too many for a traditional tunnel-style screw terminal is probably not something everyone will agree on, but I would say 3 is ok, 4 is pushing it and more than 4 is probably a bad idea.
Again, in terms of "13A" BS1363 socket terminals (and probably many other accessories), that is probably true. However, in terms of "terminal holes" in general, the following are a few snippets from an MK catalogue ........I don't think I have ever seen a manufacturer advertise a single terminal hole as having capacity for more than 3 conductors.
The most common type have a rotatable cover which enableone to choose which, and how many, of the cable entries one want to be 'open' - so maybe the idea is that it enables you chose which 3 (or less) you wish to use?I find this particularly strange with the oldschool junction boxes as they have four cable entries, yet the datasheet I found for one only specified 3 conductors per terminal.......
I agree with all that.If you want to take three spurs from the same junction box, I would suggest the Wagobox 221-4 with Wago 221-415 series terminals. ... For more than 3 spurs you could use the Wagobox XL or XLA with appropriate terminals.
Fair enough.so, in terms of the general, some manufacturer *well, at last MK) do "advertise a single terminal hole as having capacity for more than 3 conductors
The MK junction boxes have multiple terminal holes per pole rather than the traditional single slot with a screw entering from the top. I presume the figures given refer to the pole as a whole and not the individual holes.MK1131 (10A,4 term) & MK1132 (30A, 3 term) JBs
It is, but I was responding to your comment that you hadn't seen MIs specify "more than 3 conductors) -and there seem to be a good few 4s out there.... Though the 2A socket seems the only one where a single terminal hole is advertised as taking more than 4 conductors.
I agree, and probably should have mentioned that I strongly suspected that it was a typo, and probably should have been 4 (i.e. the same as for 1.5mm²) - which is why I did not 'highlight' the apparent "7"! However, that is again still greater than 3I do wonder if that is a mistake that didn't get caught/didn't get sufficient engineering review.
Good point - I'd totally forgotten that. Having now been reminded, it seems that they are specifying 2 x 1.5 mm² 'per hole' for the 4-pole ones and 1 x 4mm² 'per hole' for the 3-pole ones, which is fair enough.The MK junction boxes have multiple terminal holes per pole rather than the traditional single slot with a screw entering from the top. I presume the figures given refer to the pole as a whole and not the individual holes.
I'm not sure I understand your point. With a 4-terminal 'lighting JB', one will usually use three of them for L, S/L & N, and then the fourth one for earth/CPC, won't one?Hager's 30A 3 terminal traditional junction box does seem to be rated for 4x2.5, though strangely their 4 terminal lighting junction boxes only seem to be rated for 3 conductors per terminal which leaves an open question about earthing...........
Yes, which means you normally will have three wires in permanent live, three wires in neutral, 2 wires in switched live and four wires in earth.I'm not sure I understand your point. With a 4-terminal 'lighting JB', one will usually use three of them for L, S/L & N, and then the fourth one for earth/CPC, won't one?
Ah, good countingYes, which means you normally will have three wires in permanent live, three wires in neutral, 2 wires in switched live and four wires in earth.
You didn't mention the conductor size, but if it's rated for 3 x 1.5mm² conductors, then 4 x 1.0 mm² CPCs shouldn't be a problem - so, although I agree that that the writing of the documentation is non-ideal, electrically it should be fine.So a lighting junction box which is only rated for 3 wires per pole seems to fail at it's primary purpose, which says something about either the people who designed the product or the people who wrote it's documentation.
The design of the terminal also plays a role pf course, oldschool junction boxes only have on terminal hole (well strictly slot) per pole forcing you to have multiple wires in the same terminal . At the other extreme the push-in and lever terminals that are becoming increasingly common are generally only suitable for one wire per terminal hole.
Back in the past that might have been "good practise".One solution, and good practice - is to fit the ring cable into the terminals without actually cutting the ring cable.
Most ring final cables live under floors or are buried in walls which means that type of JB cannot be used today, as they are unaccessible.