What I mean is of course flexible cable, apologies for the incomplete description.If you mean flex, 0.75mm² is rated at 6A and 1mm² at 10A.
Yes the ratings you have quoted match with my understanding.
What I mean is of course flexible cable, apologies for the incomplete description.If you mean flex, 0.75mm² is rated at 6A and 1mm² at 10A.
I Don't see how that relates toNo need to apologise; I was just making sure.
The purpose of my question was that the flexes are 3A, 6A, 10A and 13A so other BS1362 fuse ratings are not required.
So what size fuse would be correct for a 1.4KW load on 0.75mm² cable?Why would anyone want a 7A BS1362 fuse?
6A.So what size fuse would be correct for a 1.4KW load on 0.75mm² cable?
Indeed I did. Our old toaster was 1.5KW and our previous Kettle was 1.8KW, I believe both were 0.75mm² cable. Henry is 1.4KW and also on 0.75mm² cable which gets quite warm, especially the bit that's still coiled, in the 20 minutes or so he's running for.6A.
Although you did say 1.5kW before in which case - strictly speaking - it depends on the voltage and might be too high for the 0.75mm² cable.
And not conforming to UK regs which is where I live.Yes, we have discussed before that leads supplied by the manufacturer do not come under BS7671.
However, were you fitting a new lead, or the equivalent on another appliance, I am sure you would stick to BS7671 and use larger flex.
Henry 1.4kW? Mine is only 620W also on 0.75mm² and since emigrating is only protected by a 16A OPD.
I don't understand.So 7A is the answer to the questions raised in posts 43 & 48.
#48Why would anyone want a 7A BS1362 fuse?
1.4kW @ 240V = 5.83A.So what size fuse would be correct for a 1.4KW load on 0.75mm² cable?
This is the unmodified manufacturers designed product, Henry hoover with a long and very thin 0.75mm² cable. 6A fuse not available, well not that I've seen and I wouldn't want to be running a large motor on a protective device with such a tiny margin.I don't understand.
#43
#48
1.4kW @ 240V = 5.83A.
Why would you want a 7A fuse for that when you have used a 6A flex?
Henry hoover
WINSTON Do you really want me to start picking holes in everything you say again?! No such thing. It is a Henry or a Hoover.
Use a 13A then, not sure of the relevance but you are moving the goal posts.This is the unmodified manufacturers designed product, Henry hoover with a long and very thin 0.75mm² cable. 6A fuse not available, well not that I've seen and I wouldn't want to be running a large motor on a protective device with such a tiny margin.
When would anyone ever need a 3A BS1362 fuse?Use a 13A then, not sure of the relevance but you are moving the goal posts.
I ask again - when would anyone ever need a 7A BS1362 fuse?
Possibly never.When would anyone ever need a 3A BS1362 fuse?
Well, you have to have A fuse in British plugs and to allow the use of small cables on 32A circuits.When would anyone ever need a 13A BS1362 fuse?
As so many people keep saying on here - Shuko plugs don't use fuses so we don't need any fuses in UK either.
So now you are self defeating your own statements, Initially you say a 3A cable is safe to use in a Shuko fused at 16A but then you say it's not safe on a 32A fuse.Possibly never.
Well, you have to have A fuse in British plugs and to allow the use of small cables on 32A circuits.
Unfortunately 13A is the highest rating made.
You still are not addressing the point of the odd sized fuses. Why are they made?
When would 7A be needed and 5A or 10A not suitable?