Nothing wrong with that - if I understand correctly.
No, but there are three sockets on the end of each spur which I understand is frowned upon.
Nothing wrong with that - if I understand correctly.
So would a radial.The two sockets that (I think) are on the ring have a cable in, a cable out, and the aforementioned spur.
I disagree. BS7671 requires that the cable be protected against abrasion.As far as I am aware fitting grommets is just considered good practice, not demanded by any regulation.
Indeed (and protected against all sorts of other environmental influences).I disagree. BS7671 requires that the cable be protected against abrasion.
It may be unlikely, but the fact remains that it hasn't been protected against. Personally speaking it is an early indicator to me of an absolutely horrendous job.Indeed (and protected against all sorts of other environmental influences).
However, 'abrasion' requires (usually repeated) relative movement, and with the exception of the incredibly improbable 'building movement' which has been mentioned, that is not going to happen with the fixed wiring to an accessory.
Kind Regards, John
due to their being no room to fit one.
remove the third cable... ...meaning a grommet could easily be fitted.
Three 2.5mm² T&E cables fit through a 20mm grommet just fine. Am I missing something here?
I would say that is very debatable. I would have thought that being solidly buried in plaster (and the same plaster as retains the back box) would be about as good a protection against abrasion ("scraping or wearing away") as anything else.It may be unlikely, but the fact remains that it hasn't been protected against.
That may well be true, but it's a totally different issue.Personally speaking it is an early indicator to me of an absolutely horrendous job.
Very often the plaster is not providing such protection at the point of entry to the box, though. Indeed this is the case with two different jobs I have been at in the past two days. It also smacks of crap installation practices regardless.I would have thought that being solidly buried in plaster (and the same plaster as retains the back box) would be about as good a protection against abrasion
Protection against what - earthquakes? What other than earthquakes would result in repetitive relative movement between cable and box?Very often the plaster is not providing such protection at the point of entry to the box, though.
Whether or not it represents 'crap installation practice' presumably depends whether it was done because an installer who believed that it should be done simply didn't bother or because it was the considered opinion of the installer that it was not necessary.It also smacks of crap installation practices regardless.