Mount the Wiser backplate at a suitable location near the boiler.
(1) Run a 2-core cable from the N & L terminals on the boiler or from the fused spur that feeds the boiler to the N & L terminals on the Wiser backplate. This could also be a 3-core cable including earth but the Wiser does not require an earth connection itself
(2) disconnect the 2-core cable in 1 & 2 at the boiler which currently goes to the battery powered roomstat.
(3) run a 2-core cable from the boiler 1 & 2 terminals to Wiser terminals 1 & 3.
boiler #1 to Wiser #1
boiler #2 to Wiser #3
Do NOT add any link between L & 1 on the wiser back plate. This is shown as a dotted line in the installation guide.
If you have a 5-core cable even better as that would replace the need for two separate cables from Wiser to boiler. Do not use a green/yellow cpc core for anything except an earth connection.
I have referenced this to assist on the wiring
(1) Run a 2-core cable from the N & L terminals on the boiler or from the fused spur that feeds the boiler to the N & L terminals on the Wiser backplate. This could also be a 3-core cable including earth but the Wiser does not require an earth connection itself
(2) disconnect the 2-core cable in 1 & 2 at the boiler which currently goes to the battery powered roomstat.
(3) run a 2-core cable from the boiler 1 & 2 terminals to Wiser terminals 1 & 3.
boiler #1 to Wiser #1
boiler #2 to Wiser #3
Do NOT add any link between L & 1 on the wiser back plate. This is shown as a dotted line in the installation guide.
If you have a 5-core cable even better as that would replace the need for two separate cables from Wiser to boiler. Do not use a green/yellow cpc core for anything except an earth connection.
I have referenced this to assist on the wiring