Update : So, I got gas engineer to check the pressure of the expansion vessel.
He checked and confirmed pressure of the expansion vessel is fine and put fernox leak sealer.
But still today the pressure went down close to zero when system was cold and no usage around 3pm
however when i start heating or hot water with out topping up, the pressure goes to 1 bar without topping up.
is still this a problem? is the water leaking?
when pressure automatically goes to 1 bar without topping up during hot water or heating running.
He checked and confirmed pressure of the expansion vessel is fine and put fernox leak sealer.
But still today the pressure went down close to zero when system was cold and no usage around 3pm
however when i start heating or hot water with out topping up, the pressure goes to 1 bar without topping up.
is still this a problem? is the water leaking?