As previously stated you need to check for any bad connections on the eBus wiring and the controller, especially the pins on the back of the controller. If the boiler loses connection or sees a blip in the requested temperature, even for a split second, then the boiler pump will start. It then runs for the duration set in D.1. At this point, that is the S.7 pump over-run you are seeing. S.7 always follows S.1, S.2, S.3 or S.4. An intermittent connection is the most likely cause, followed by a controller and/or boiler PCB fault.