Hi,
First post so please forgive me where I go wrong.
Wondering if anybody has some detailed knowledge about a suspected bypass valve that is not working as I expect it to.
To elaborate: I have a Vaillant Ecotec 637 boiler, with an S-plan layout. Large 5 bed, 3 bath detached, decent insulation. 14 Radiators, 210l Cylinder. House seems to be rather slow to heat up (1 degree per hour, approx). Once warm boiler copes easily.
I was investigating why the house is rather slow to warm up and I was measuring the flow and return temperatures with the system running stable and all radiators fully open, and managed to balance the radiators so they all got approximately equal flow of hot water.
Roughly doing the maths I had the impression the boiler wasn't working as hard as it could/should be with the return being over 12 degrees colder than the flow. It seems to be happy pottering along at minimal power, but maintaining flow at the set temperature.
Menu in the boiler can report return temperature and this reports some 10+ degrees higher return temperatures than I measure on the return pipe entering the boiler.
I suspect the built-in bypass valve is never fully closing, even with all radiators fully open and hot water cylinder heating up. I would expect with all these pathways fully open for the hot water to flow easily around the system and the automatic bypass valve to be fully shut.
From cold it goes to full power for a a good few minutes but reasonably quickly then settles down to minimal to lowish power.
I've asked an engineer to have a look at the boiler and he said all was working ok, he didn't find any restricted flow etcetera. I've asked him to check with his temperature sensor and he confirmed the return before pump and bypass valve is 13 degrees lower than the return just after pump and bypass valve. (All this is inside the boiler).
This with all radiators open and circuit to hot water cylinder open too.
The engineer gave Vaillant a call to ask if increasing the ABV setting would help and they said that is hardly ever required but he could try. Increasing the setting to max (350 mBar I believe) did reduce the temperature difference measuring just before and right after ABV and Pump to about 10 degrees.
Vaillant didn't mention if this large temperature difference before and after ABV is normal or not.
Can anybody confirm this is normal or abnormal behaviour for this system?
Is the ABV supposed to let by this much flow back in to the return? This way the water returning to the heat exchanger is consistently hotter than is necessary, and all my efforts to get the return flow cool enough to maximise the boiler's efficiency seem to be in vain?
Any other suggestions what might be worth investigating?
Many thanks in advance!
Waldo
First post so please forgive me where I go wrong.
Wondering if anybody has some detailed knowledge about a suspected bypass valve that is not working as I expect it to.
To elaborate: I have a Vaillant Ecotec 637 boiler, with an S-plan layout. Large 5 bed, 3 bath detached, decent insulation. 14 Radiators, 210l Cylinder. House seems to be rather slow to heat up (1 degree per hour, approx). Once warm boiler copes easily.
I was investigating why the house is rather slow to warm up and I was measuring the flow and return temperatures with the system running stable and all radiators fully open, and managed to balance the radiators so they all got approximately equal flow of hot water.
Roughly doing the maths I had the impression the boiler wasn't working as hard as it could/should be with the return being over 12 degrees colder than the flow. It seems to be happy pottering along at minimal power, but maintaining flow at the set temperature.
Menu in the boiler can report return temperature and this reports some 10+ degrees higher return temperatures than I measure on the return pipe entering the boiler.
I suspect the built-in bypass valve is never fully closing, even with all radiators fully open and hot water cylinder heating up. I would expect with all these pathways fully open for the hot water to flow easily around the system and the automatic bypass valve to be fully shut.
From cold it goes to full power for a a good few minutes but reasonably quickly then settles down to minimal to lowish power.
I've asked an engineer to have a look at the boiler and he said all was working ok, he didn't find any restricted flow etcetera. I've asked him to check with his temperature sensor and he confirmed the return before pump and bypass valve is 13 degrees lower than the return just after pump and bypass valve. (All this is inside the boiler).
This with all radiators open and circuit to hot water cylinder open too.
The engineer gave Vaillant a call to ask if increasing the ABV setting would help and they said that is hardly ever required but he could try. Increasing the setting to max (350 mBar I believe) did reduce the temperature difference measuring just before and right after ABV and Pump to about 10 degrees.
Vaillant didn't mention if this large temperature difference before and after ABV is normal or not.
Can anybody confirm this is normal or abnormal behaviour for this system?
Is the ABV supposed to let by this much flow back in to the return? This way the water returning to the heat exchanger is consistently hotter than is necessary, and all my efforts to get the return flow cool enough to maximise the boiler's efficiency seem to be in vain?
Any other suggestions what might be worth investigating?
Many thanks in advance!
Waldo