As luck will have it last night was a gentle 10 degrees, nothing like the -4 the nights before...
So not sure if there's any difference, as the house didn't cool down much under 19 degrees during the night.
Ok, set d0 to 20, let system cool down and monitored it for the better part of an hour:
Hope you can see the attached image, tried copy/paste but that didn't work.
I've checked status, d40, d41, and return pipe temp every minute. Flow pipe measured is consistent with d40 so I've left that out (shows my thermometer is at least reasonably accurate...).
As far as I can tell this shows it is increasing the temperature 14 degrees with 20kW power.
Radiators feed all get warm at about the same time, but it takes quite some time for them to get hot.
After over an hour they are pretty hot the water going in is in around the 70 mark, water going back out around 50 to 55 on average over all radiators.
Boiler reduces power after around half an hour. I've checked after an hour and the return pipe is around 55 degrees, and boiler is running at minimum power, 12.5 kW (according to manual)
Any thoughts?
thanks
Waldo