A fault does not make something an e-c-p.A fault which places a potential on, say, a kitchen tap could in turn introduce that potential to the bathroom plumbing.
A fault does not make something an e-c-p.A fault which places a potential on, say, a kitchen tap could in turn introduce that potential to the bathroom plumbing.
A fault does not make something an e-c-p
They are; we do.Of course it doesn't, but a fault could result in a fatality and therefor common sense would be to take steps to ensure as far as possible that faults are contained so as to reduce the risks of injury or death.
As stated many times before, that risk is considered less than the alternative - touching a live conductor at the same time as an unnecessarily earthed pipe, tap, window frame, door knob, spoon etc.A couple of years ago after a plumber re-plumbed a house a measurable potential difference existed between two taps in the kitchen. It was due to capacitive coupling between pipes and cables, harmless but had pipe against cable resulkted in a fault that tap could have been Live with the other tap at Earth potential. Extremely unlikely that fault would occur but the cost of two Earth strap and a bit of cable to bond the taps together gave the owner peace of mind.
As stated many times before, that risk is considered less than the alternative
NoSo are you saying we should always bond metallic pipe work regardless of whether or not it is an e-c-p?
That is most unfortunate but does not negate the fact that the alternative may result in 10 in 10,000 (I don't know the figure).That argument has some validity, but tell that to the family of someone seriously maimed due to an incident that was caused by a "1 in 10,000" fault when 5 minutes and 50p of bits would have prevented that "1 in 10,000" fault going un-noticed and repaired before it was discovered when it caused injury.
Then it does not get bonded.Of course it doesn't
Indeed, with increased used of plastic couplings, plastic tap fixings etc. there's far more potential (no pun intended) for such things to happen than in the past when there was a good chance that every bit of plumbing throughout the house was all bonded together electrically.With bits of plastic plumbing mixed with copper plumbing that potential could be on the cold tap while the hot tap is being held at ground ( Neutral ) via copper pipe to the hot water cylinder and it's earth immersion heater.
Even if a fault causes that part to introduce a potential into some particular location which would not otherwise be there?A fault does not make something an e-c-p.
I am not sure which such things to happen you have in mind.Indeed, with increased used of plastic couplings, plastic tap fixings etc. there's far more potential (no pun intended) for such things to happen than in the past when there was a good chance that every bit of plumbing throughout the house was all bonded together electrically.
As above, if it is not an extraneous-c-p it can't.Even if a fault causes that part to introduce a potential into some particular location which would not otherwise be there?
As in Bernard's example. Say you have continuous continuity from the immersion heater tank to the hot tap, which is therefore earthed by way of the feed to the immersion heater, but plastic couplings have left that unbonded cold piping floating, or in reality earthed via the relatively high resistance of various stray paths through the fabric of the building. But if there's still a solid metallic path between the cold taps in different locations, something which livens the cold pipework in, say, the kitchen (a frayed kettle cord, perhaps) will leave the cold pipework at the bath live at 240V while the hot is still earthed by way of the immersion heater.I am not sure which such things to happen you have in mind.
Why not? The possibility of a metal appliance casing becoming live that way is taken into account by requiring either earthing or double insulation.Bernard often speaks of pipes becoming live by coming into contact with a live conductor (this does not have to be considered in normal circumstances)
But if the pipe is earthed only via stray building paths, the OPD won't operate. Even an RCD might not (over 8000 ohms or so for a 30mA, 2400 ohms for 100mA etc.).rather than becoming live because of a fault to an exposed-c-p only until the OPD operates - when the pipe is already connected to a CPC of an appliance.
If it's conductive, it can always introduce a potential into the area at one end of it if some potential is applied at the other end.As above, if it is not an extraneous-c-p it can't.
Well, if those stray paths cause the cold pipe to be within the limits to be considered an extraneous-c-p, although not likely, then, in a bathroom but not in a kitchen, supplementary bonding will be required.As in Bernard's example. Say you have continuous continuity from the immersion heater tank to the hot tap, which is therefore earthed by way of the feed to the immersion heater, but plastic couplings have left that unbonded cold piping floating, or in reality earthed via the relatively high resistance of various stray paths through the fabric of the building.
That scenario is not required to be considered as it is deemed less hazardous than you touching the frayed lead and a wrongly bonded - earthed - isolated part.But if there's still a solid metallic path between the cold taps in different locations, something which livens the cold pipework in, say, the kitchen (a frayed kettle cord, perhaps) will leave the cold pipework at the bath live at 240V while the hot is still earthed by way of the immersion heater.
Because it is not an exposed-c-p as it is not part of the electrical installation.Why not? The possibility of a metal appliance casing becoming live that way is taken into account by requiring either earthing or double insulation.
Well, it is not a likely occurrence and, as I keep saying, that is considered less of a hazard than the opposite scenario.But if the pipe is earthed only via stray building paths, the OPD won't operate. Even an RCD might not (over 8000 ohms or so for a 30mA, 2400 ohms for 100mA etc.).
I refer the honourable gentleman to the reply I gave a moment ago.If it's conductive, it can always introduce a potential into the area at one end of it if some potential is applied at the other end.
Bernard often speaks of pipes becoming live by coming into contact with a live conductor (this does not have to be considered in normal circumstances)