This is Honeywell's recommended wiring (ignore pump overrun - you boiler doesn't have it):
Yep, that is how it is! Very clear diagram
This is Honeywell's recommended wiring (ignore pump overrun - you boiler doesn't have it):
Please confirm that your boiler is a Glowworm Spacesaver 50 MkII - GC No 41-313-03 (on the data plate or Manual).
Just wanted to confirm that the connections were the same as other Spacesaver boilers. Unfortunately the Installation Manual is not available online.Does this affect the control of it?
Don't understand what you mean by "Linked (L)". There is only one jumper on the back which is in either the G or P position.The programmer is set to Gravity fed (G) and Linked (L) with the jumpers on the back.
I have managed to answer my own question.Don't understand what you mean by "Linked (L)". There is only one jumper on the back which is in either the G or P position.
There are two ways of getting CH only:Thanks, yes missing wire now installed but If I+P are set, the timer works but setting 'CH only' illuminates the HW light too. Guess as previously suggested it depends on the sequencing.
There are two ways of getting CH only:
Does the HW light come on in both scenarios?
If it does, contact Drayton and seek their advice:
Customer Services 0333 6000 622
Technical 0333 7000 622
Email [email protected]
Not really in this instance, the sequencing should be correct if controlled by the programmer, for example it won't allow hot water 'on' and hot water 'off' to be live at the same time. I only mentioned the sequencing when you were making connections of the grey wire to a live that wasn't via the programmer during fault finding.Guess as previously suggested it depends on the sequencing.