Agreed, but as the cable in a ring only has to have a CCC of 20A (albeit with the minimum csa of 2.5mm² still for BS3036 30A fuses - 2 x Iz for an hour) does it not work out the same?Yes, it would provided that the 'over-current tolerance' of the switch were the same as is deemed to be the case for a cable (e.g. able to happily carry 1.45 times its Iz for an hour). However, as you go on to say, we're actually talking about "a switch which has a current rating < the cable" . As you say ..
However, you mentioned short-circuit currents so are switches made with that in mind or are they expendable?
I was - with regard to PFC.Are you talking about a 'spur cable' with downstream OPD protection (as in plug fuses etc.)?
Are they? It would seem not - with dimmers anywayNot if they were treated like cables - i.e. were required to have over-current protection which would prevent a high current flowing for long enough to cause damage to them.
Yet, it is.In many ways, it is (common sense). As you know (from some of my talk about 1A BS1362 fuses ) what I have thought deviates a bit from common sense is the concept/belief that over-current protection "is only there to protect cables" -
Because they are not part of the fixed wiring to which one may connect various appliances which are not mentioned.why not everything else in the circuit (which I suppose is probably what this reg, previously unfamiliar to both of us, is trying to say)?