Not a manufacturer with a good reputation, then?!
The cylinder stat is low power and can be covered or not. But no need to cover it.
But the immersion heater connection box should never be covered by insulation.
As I predicted your cyl stat is correctly connected to turn off the boiler and pump when the cyl has reached the set temperature.
But the deficiency in that very simple system is that when the heating is on the cylinder is always on. Potentially heating the cylinder up to a higher than the recommended maximum of 60 C. Wasting energy and giving a risk of scalding. Quite apart from the inconvenience of fluctuating hot water temps.
Tony
Correct.
There is a problem though. In the winter the pump and boiler will need to be operating in order to heat the radiators. However, your installation (i.e. without a motorised valve for the hot water cylinder) means that water from the boiler will also be being circulated through the hot water cylinder. So even when the cylinder thermostat switches off, it won't be doing anything because the central heating will keep the boiler and pump running and will continue to circulate water from the boiler around the hot water cylinder.
Not sure how they would have stopped the water circulating through the cylinder, though.
fooking £10k your pulling my plonker right , where do you live ill do it for 9kI also have inherited an old system: One pipe, Ideal Mexico. Prior owners had a BG cover so knowing how cheap it is i have continued with it. If you renewed it they would maybe have fixed it. Last service they did recently guy said it in top shape. To replace with 2 pipe would mean moving boiler to the loft as it couldn't be where it is for regs. (One floor place) Because of work involved, said it would be expensive: £10k (!) Boiler/scaffolding required/two pipes (plastic though i have one copper already) Haven't heard back after 4 months now! Am going to attempt to it 2 extra rads where there should be heat and will post for advice. Lot of people say these systems are fine. Mine heats up quickly and is v hot. By the time you get your money back if you update it the new boiler would probably need replacing....However your system does sound older.