Only from sep 2020 tho!The functional earth lead is incorrectly identified by colour. It should be pink (formerly cream).
Only from sep 2020 tho!The functional earth lead is incorrectly identified by colour. It should be pink (formerly cream).
Its been Cream since at least the 80'sOnly from sep 2020 tho!
Indeed it has, and as I wrote, it’s changing to pink in sep 2020Its been Cream since at least the 80's
I've been finding white, cream, green or green/yellow for agesIndeed it has, and as I wrote, it’s changing to pink in sep 2020
By virtue of what (regulations or whatever)? Table 51 of BS7671:2018 gives the colour as cream, and I'm not aware that it is going to be amended by/in September 2020.Indeed it has, and as I wrote, it’s changing to pink in sep 2020
Thanks - I was not aware of that.There is a corrigendum which has been issued (Dec 2018), which lists the eleven corrections to be made to bs7671 https://electrical.theiet.org/media/2063/bs-7671-2018-corrigendum-dec-2018.pdf
Maybe, but as I read it, as of September 2020, the post-corrigendum BS7671 will read "Cream/Pink"!BS EN 60445 doesn't mention cream so i assume that cream will no longer be acceptable.
Hmmm. Is that meant to be a general statement applying to the identification of all conductors (including protective ones)? If so, will we no longer be allowed to use G/Y after September 2020 ?!!To quote from BS EN 60445:
6 Identification by colours
6.1 General
For identification of conductors, the following colours are permitted: BLACK, BROWN, RED, ORANGE, YELLOW, GREEN, BLUE, VIOLET, GREY, WHITE, PINK, TURQUOISE.
NOTE This list of colours is derived from IEC 60757.
I'm getting confused! You are surely not saying that that list of 12 colours given in 6.1 of 60445 are all appropriate for functional earths??BS EN 60445 only refers to functional earth colours, not general wiring colours.
That sounds clear enough - but, as I've said, if I'm reading the corrigendum correctly, come September BS EN 60445 and BS 7671 will say rather different things - since it looks as if BS 7671 will then say "Cream/Pink", with no expressed preference for either of those colours.As i understand it, according to BE EN 60445, all functional earths will now require a pink functional earth lead from sep 2020
"6.2.5 Functional earthing conductor
For colour marking of a functional earthing conductor the preferred colour is PINK."
I'm getting confused! ..... You are surely not saying that that list of 12 colours given in 6.1 of 60445 are all appropriate for functional earths?? .... Since it looks as if BS 7671 will then say "Cream/Pink", with no expressed preference for either of those colours.
Kind Regards, John
Yes, that would eliminate any possible ambiguity, but I would imagine that the great majority would interpret "Cream/Pink" and meaning the same as "Cream or Pink" - although maybe a troublesome minority would interpret it as meaning "Cream and Pink stripes" (as in G./Y)!!Surely a more sensible way of eliminating ambiguity - if that was the intent - would have been to use the term "... Cream or Pink..."