BG - changed the diverter valve due to leak.
Next day hot water reached 80 then boiler shut down and water went cold . Had to turn the tap off then back on to get a burst of hot water
BG - came back said heat exchanger needed changing and a power flush
Since the boiler and all the rads and pipe work are 4 years old - I didn't believe this. (Fernox inhibitors etc in system)
Asked BG to check the PCB after reading this forums old posts. He said that it was fine.
Got a local GS engineer round , he fitted a salamander mains booster for no reason at all and didn't fix the issue.
He checked the domestic water heat exchanger and said it was fine and the water in the system is fine.
Problem still there next day.
Bought a new heat exchanger , I fitted it last night.
Visually flow tested the new one vs the old one not much difference
Symptoms didn't change with new heat exchanger
Central heating works fine all the the above issues.
Woke up this morning and disconnect and reconnected flow sensor plug.
Now all of a sudden I can have a 10-15min shower no problem.
Haven't attempted a bath yet----which has been a issue since the dv valve was changed.
Next day hot water reached 80 then boiler shut down and water went cold . Had to turn the tap off then back on to get a burst of hot water
BG - came back said heat exchanger needed changing and a power flush
Since the boiler and all the rads and pipe work are 4 years old - I didn't believe this. (Fernox inhibitors etc in system)
Asked BG to check the PCB after reading this forums old posts. He said that it was fine.
Got a local GS engineer round , he fitted a salamander mains booster for no reason at all and didn't fix the issue.
He checked the domestic water heat exchanger and said it was fine and the water in the system is fine.
Problem still there next day.
Bought a new heat exchanger , I fitted it last night.
Visually flow tested the new one vs the old one not much difference
Symptoms didn't change with new heat exchanger
Central heating works fine all the the above issues.
Woke up this morning and disconnect and reconnected flow sensor plug.
Now all of a sudden I can have a 10-15min shower no problem.
Haven't attempted a bath yet----which has been a issue since the dv valve was changed.