yes thats it doesnt matter how it is fitted , can you hear or feel it turning when the heating and HW are switched on ?
Your boiler doesn't have a pilot light, the green light tells you it is lit.
Is the blue light flashing on the front of the boiler?
That suggests the boiler has no demand for heat, problem in airing cupboard probably, mid-position/zone valve/ control problem.Neither light comes on at all
Your earlier posts indicated the boiler did try to fire up ,but not for long ??Neither light comes on at all
Perhaps try the manual overide on the zone valve in picture 8 whilst the timer/stat is in a call for heat mode.
Have someone watch the boiler whn you push the lever. it may fire, indicating that the sycronous motor in the valve is buggered.
Common fault in my zoned heating (Myson valves are pants for this) and an easy, cheap fix.
Worth a try?
Aerjec may be blocked ,water starvation ?
Your earlier posts indicated the boiler did try to fire up ,but not for long ??
Sorry, didn't spot this message.
We topped up the small tank in the loft last night, unsure if this is what got the boiler going again, but it'a gone again this evening (see comment just now). Unsure if this could still be the problem?
The head tank has emptied?
Plumber time.
switching it to maual wont damage anything, but as soon as ther is a change in demand from you programmer/thermostats, if the motor is working , it will return to auto